Hello m.dani; The reason that you cannot simulate your program on a S7-400H system might be simply that PLCSim v5.4 does not support H-Systems. See the screenshot below, taken from the S7-PLCSim v5,4 manual, section "Differences from a "Real" PLC": https://support.industry.siemens.com/cs/ww/en/view/54667828/28932144779 One suggestion: You could modify your hardware configuration to a single-CPU system (no redundancy I/Os or OBs) and try to simulate that on PLCSim. All functionnalities for your final project will not be available of course, you would need to wait for the actual hardware to test them. Hope this helps, |