Hello Mastermind; The S7-412-5H CPU has 512 kb integrated code memory/512 kb for data, whereas the S7-414-5H has 2MB for code and 2MB for data. CPUs 416-5H and 417-5H have much more integrated memory, but at a much higher price. See the technical data for the S7-400H technical data, in this link. and the screenshot below: https://support.industry.siemens.com/cs/us/en/view/82478488/68709584267 If ypu have a standalone CPU, you can simply modify the present CPU for the seklected replacement model in the Hardware Configuration, then download to the new CPU. If this is a redndant system with 2 CPUs, both CPUs must be identical when ypu update the system. If this is a PCS 7 installation, you culd also replace uour existing H-CPU with a S7-410-5H., and select the approproate number of PO as part of the memoru card used in the project. Hope this helps, |
Last edited by: dchartier at: 11/26/2021 21:14:39 |
|
1/10/2022 8:31 AM | |
Joined: 2/25/2019 Last visit: 10/23/2022 Posts: 7 Rating: (0) |
I replaced it but it gave me error What also I should replace |