4/3/2011 7:06 PM | |
Joined: 3/21/2006 Last visit: 11/1/2024 Posts: 10229 Rating: (1181) |
Perhaps might helps - FB126 "PNIODiag": 26996747. |
4/4/2011 2:09 AM | |
Posts: 19 Rating: (0) |
Thanks for your link. However my system is located in racks connected together with IM360-IM361 and not Profibus DP or Profinet. Cheers,
|
4/6/2011 3:47 AM | |
Posts: 19 Rating: (0) |
Hi everyone, Does anybody can help me please? I thought it was a simple question, and I guess a lot of people did implemente that already. Thank you ver much
|
4/6/2011 11:53 AM | |
Joined: 4/22/2010 Last visit: 10/17/2024 Posts: 5697 Rating: (715) |
If you you have modules with diagnostics enable that in the hardware config. When a fault occurs, OB 82 is triggerd (must be in PLC or PLC will stop) In this OB you can write a program to show witch module has an error. see the attached helpfile for more information. Best regards, Marcjan AttachmentOB82.pdf (194 Downloads) |
Problem solved? |
|