8/2/2017 10:45 AM | |
Joined: 10/12/2009 Last visit: 6/1/2024 Posts: 23 Rating: (0) |
Hi, Can i use S7-FH CPUs as single, i should use H-CPU but I don't want to use a redundant structure, i need the IEC61511 certification for our project and this qualification have siemens certificate no: Z10 16 06 20080 004. All PLCs written as H-CPU in the attachment of the certifica, but i don't need redundant structure so can i use H-CPU as single. thanks, AttachmentZ10_16_06_20080_004_sig.pdf (72 Downloads) |
8/2/2017 2:40 PM | |
Joined: 6/14/2006 Last visit: 4/29/2024 Posts: 301 Rating: (60) |
Yes, you can! |
This contribution was helpful to1 thankful Users |
8/2/2017 3:18 PM | |
Joined: 9/27/2006 Last visit: 6/2/2024 Posts: 12259 Rating: (2670)
|
Hello cemo; Details on the configuration of a S7-400H station in stand-alone mode can be found in Appendix B of the Fault Tolerant S7-400H System manual: SIMATIC Fault-tolerant systems S7-400H Configuring stand-alone mode Requirement: No synchronization module may be inserted in the fault-tolerant CPU. Procedure:
For help on procedure refer to the Help topics in SIMATIC Manager. Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |