9/23/2019 4:22 PM | |
Joined: 4/18/2019 Last visit: 8/1/2024 Posts: 3 Rating:
|
Hi, Can anyone tell me the difference between this 1500 card against the older S7-300 model 6ES7331-7PF01-0AB0 in relation to the Glass Furnace Industry. We think we have identified a major flaw in the new 1500 card where we are experiencing up to 90 V AC on the thermocouples when the thyristors fire across the glass at 1200degC. We never had this issue when using the S7-300 cards. The website states this is a suitable replacement. https://support.industry.siemens.com/cs/ie/en/view/109482719 Any advice or help appreciated as we are getting very little response from Siemens. Thanks.
|
Last edited by: The Helping Hand at: 09/23/2019 16:38:48Last edited by: The Helping Hand at: 09/23/2019 16:39:24Optimized Link. |
|
9/23/2019 7:28 PM | |
Joined: 7/7/2010 Last visit: 8/7/2024 Posts: 15068 Rating:
|
What filtering do you use (or did you use) on the S7-300's 331-7PF01 TC inputs? What filtering do you use on the s7-1500's 531-7PF00 TC inputs? I suspect your S7-300 system was not responding fast enough to notice any problem, but on the s7-1500, things are much faster, which resulted in your measuring the high common mode voltage induced from the induction furnace powered by the thyristors. If you measured the s7-300 system at the same time in the same way, what voltage would you see? If you do not know, perhaps you can assume it is 90 VAC. Are you using shielded TCs? Are you following the Siemens suggestions for wiring of TCs with the sense lines, proper terminal times, proper wiring type, or did you just swap hardware and hook it back up?
|
science guy |
|
Follow us on