7/8/2013 9:26 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (875) |
Hello Experts, Which criterias are to be looked uponwhile selection ofCT & PT to be connected with SENTRON make PAC 3200 power monitoring device? Please find attached here with the sheet of accury values of PAC 3200 meters are specified. As per manual, these values depends upon CT & PT connected. So can any one help? Thanks in advance. DEEP. AttachmentSentron PAC 3200 PMD accuarcy value.pdf (535 Downloads) |
Last edited by: PISCEAN 2010 at: 7/8/2013 9:38 AMAttachement added |
|
7/8/2013 10:51 AM | |
Joined: 1/21/2013 Last visit: 6/6/2024 Posts: 4620 Rating: (705) |
Hi DEEP, Have a look go to page 8: Instrument Transformer Basic Technical ... - GE Digital Energy |
7/8/2013 11:11 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (875) |
Hello Ste39 , |
7/8/2013 11:30 AM | |
Joined: 1/21/2013 Last visit: 6/6/2024 Posts: 4620 Rating: (705) |
Hi DEEP, In simple terms more than the class of the current transformer is low and more than accurate. |
7/9/2013 6:13 AM | |
Posts: 262 Rating: (45) |
Hi, If I refer to IEC 60044-1, we found the following precision classes for measuring CTs:-Classes 0.1, 0.2s, 0.2, 0.5, 0.5s, 1, and 3. Hence, we may need the current transformer with higher precisions - for PAC3200 +/- 0.5% and for PAC4200 +/- 0.2% to get the desired result like for 99.6A you may need a CT and PAC 4200 both with the 0.2% of accuracy. Attached is the catalogue extract of “4M Protective and Measuring Transformers” catalogue where-in you will find high precision CT’s detail i.e. 0.2 or so. You can also google it for the local SL representative to get more info on pricing/ availability etc.
AttachmentSiemens_CT.pdf (522 Downloads) |
This contribution was helpful to2 thankful Users |
Follow us on