9/9/2020 11:27 PM | |
Joined: 2/1/2010 Last visit: 9/11/2024 Posts: 150 Rating: (71) |
Uzi From either 8.2 SP1 or 9.0 if you exceed the limits for the changes download you are no longer given the option to ignore the limits and download changes anyway. So if you ever did OS changes downloads before and you were >1xxx / 1000 for any of the items, you were technically violating the recommendation and doing it. Now Siemens has (IMO correctly) taken this option away to improve system stability. The new server sync status makes it easier for you to know when you can do the second entire OS download of your server pair. Make sure you always wait for the sync to be completed. Yes it is an extra ~30 minutes of your time in most cases, but considering you don't have to worry about changes downloads hanging up or your system crashing later this is much better. What issues are you observing/experiencing during entire downloads? It is perfectly normal, and in fact one of the whole points of server redundancy to allow one server to go down and support all clients while the other has maintenance (such as downloading). |
Last edited by: RVS.wick at: 09/09/2020 23:27:44If my post helped you, please rate. Thanks. |
|
9/21/2020 10:23 PM | |
Joined: 3/14/2008 Last visit: 9/12/2024 Posts: 2095 Rating: (936)
|
Hi, Downloading to the server(s) which allows only full download is strange, at least if you did not do any changes as described below:
Can you upload the diagnose files in a .zip file which are listed under: C:\Program Files (x86)\Siemens\WINCC\diagnose I can take a look, maybe I'll find something. |
If I could help you, you can use the RATE button. Thank you. |
|
9/24/2020 6:14 PM | |
Posts: 3 Rating: (0) |
Here it is .zip file of diagnose. appreciated your help. Attachmentdiagnose.zip (134 Downloads) |
9/25/2020 7:49 AM | |
Joined: 3/14/2008 Last visit: 9/12/2024 Posts: 2095 Rating: (936)
|
Hi, I see that there is a problem with connection: "FSC09". It regularly gives error: "0xFFDF 410E!" which can mean one of following things:
After the error, a message is displayed that connection FSC09 is not redundant: "Redundancy error: Connection "FCS09" is not redundant!" It looks to me something is wrong with the redundant configuration. Maybe you can check the redundancy settings like configured network card, redundant configuration in WinCC Explorer for both servers, Simatic Shell settings. Did it worked before? download change? Maybe you can upload the diagnose files from the ES as well. Maybe something shows in there. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |
Follow us on