6/30/2013 11:02 PM | |
Posts: 62 Rating: (4) |
Dear Friend, SetTagByteWait & SetTagByte are the two Functions in the wincc C scripts. SetTag Wait Function is wait for completing the process of Set the value.also this will read back the Act State from the Tag.then it will go for next step. but this have the DrawBack when u r using this for set more tags.due to this function it will load your Screen.some times u r screen will take mor time to update the Status. Set Tag will Send request to set the value but it will not look Back the value. Regards, Avinashkrishna Bhimavarapu |
This contribution was helpful to1 thankful Users |
7/1/2013 2:07 PM | |
Joined: 10/3/2010 Last visit: 4/29/2024 Posts: 1552 Rating: (188) |
Even in the newest manual WinCC V7.2 WinCC: Scripting (VBS, ANSI-C, VBA) it's still written as :
|
B r g d s , |
|
This contribution was helpful to1 thankful Users |
7/1/2013 2:45 PM | |
Joined: 10/3/2010 Last visit: 4/29/2024 Posts: 1552 Rating: (188) |
Hey Tornes, sometimes Siemens English manuals contain translating errors and German manuals can be a solution now and then. For your information, I just checked the German manuals but it says the same.
If you really want to be sure, you can always create a free Support Request, usually they responds within the next day for things like this. |
B r g d s , |
|
This contribution was helpful to1 thankful Users |
Follow us on