Posts: 103 Rating: (0) |
DEAR EXPERTS PLS CLEAR BELOW PARAMETER ADDRESS WHICH IS USED IN SFC 14,15 P#DIX30.0BYTE 12 THANX |
8/29/2011 9:27 AM | |
Posts: 2348 Rating: (263)
|
pointer to area 12 bytes length, staring with byte 30 in DI-block. Number of datablock is stored in DI register. |
8/29/2011 10:06 AM | |
Joined: 1/28/2009 Last visit: 5/20/2024 Posts: 6840 Rating: (1359) |
Dear member Please also check the attachment which is a part of STEP7 online manual:
Best regards Attachmentsfc14.zip (368 Downloads) |
8/30/2011 12:25 PM | |
Joined: 3/21/2006 Last visit: 4/25/2024 Posts: 10228 Rating: (1181) |
cpu313c-2dp You will need in PLC an input in case of reading drive output and opposite - in PLC an output in order drive to read it via input. |