1/21/2010 10:31 AM | |
Joined: 8/25/2006 Last visit: 10/14/2024 Posts: 2209 Rating: (279) |
Hello. I don't know S5 plc well, but I read in documentation that IM318 is interface module for ET200U system, so as I understand IM318 may be only as slave on DP. And in your configuration IM318 is slave for S5-plc, which is master for the IM318 and CS61 (I think). So if S5 receive data as master from CS61, I think there is no problem to connect S5 with S7 and resend requied data from S5 to S7 plc. All gsd files you can find here (also for ET200U (IM318B and IM318C)). |
Last edited by: KSN at: 2/9/2010 4:38 AM |
|
1/21/2010 3:38 PM | |
Posts: 131 Rating: (0) |
yes you're right: the im318 is a master to Simadyn. thank you very much for ur help. |
2/9/2010 6:00 AM | |
Joined: 8/25/2006 Last visit: 10/14/2024 Posts: 2209 Rating: (279) |
May be you can attach here your initial configuration file (.ET2), made in ComProfibus 2.1? |