Industry Online Support
Technical Forum
6/1/2010 11:17 AM | |
Posts: 2964 Rating: (482) |
Hello.... Alarm 300501 "maximum current monitoring" 1.Serious fault occured during the actual current measurement. 2. maximum current thershold was exceeded while the rotor positionientifaiction was active(Feed Drive Only) Check the IGBTS of the power module 80A by keeping the multimeter in diode mode. I am attaching you the details. check it out... AttachmentChecking procedure for FDD-MSD Module.pdf (653 Downloads) |
This contribution was helpful to1 thankful Users |
11/30/2016 2:04 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4767 Rating: (123) |
New question published by AutoGen_922730 is split to a separate thread with the subject How can I change vaLues p-095 and how can I set aLL parameter to defauLt factory?. Best regards |
Follow us on