3/25/2016 6:22 AM | |
Posts: 57 Rating: (0) |
Sir We are using SIMOREG 6RA70 drive for mill motor.where we are using 750KW motor for mill ETR and DTR rotation. For filed we are suing separate drive. Drive is tripping on F67 fault. and same time armature drive is tipping on F005 fault. further checked in further drive, it's 1 fan is not working and we are not having spare fan of 24V. so we provide external cooling fan with external supply. And as per attached manual P820.10=67 done ( bypassed the fault). Drive is not tripping. my doubt is 1.wheter it is safe or not to run the mill. 2.before changesin drive P820.10 was set to 68 wthat is the meaning of P820.10=67 or 68. 3.r13=36 4.fault memory r947.9=40 and r948.9=67.please guide Attachmentfaq_6ra70_fault_diagnostics_en.pdf (492 Downloads) |
Last edited by: Vishal Jakkani at: 3/25/2016 6:29:14 AM |
|
3/25/2016 8:27 AM | |
Joined: 8/25/2006 Last visit: 4/29/2024 Posts: 2203 Rating: (277)
|
1,2,3 - yes. |
This contribution was helpful to1 thankful Users |