Hi, As from TIA V17 it is possible to work with a WinCC Unified as OPC UA server for data and alarms (DA, A&C), both, in Runtime and HMI. It is possible to use signed and encrypted communication and authentication of client. Configuration steps: General configuration:
TIP:
(there is no option for “none” , that means, there is no open access) (Sign means data packets are signed with the certificates but not encrypted; SignAndEncrypt means data packets are signed and encrypted with the certificates). Certificate handling:
Main steps:
For the first client’s access to the PC Runtime the steps are:
TIP:
Sample program WinCC Unified as server and UAExpert as client project backup. AttachmentOPC Server PC.zip (251 Downloads) |