Industry Online Support
Technical Forum
3/24/2011 6:23 AM | |
Joined: 3/21/2006 Last visit: 12/2/2024 Posts: 10229 Rating: (1181) |
Hello Bruno, In PLC side you need only to assign the type of AO and to make hardware connection to AI in Simoreg/Sinamics drive. The important thing is the type of AO and AI to correspond each other. (etc. 4-20mA). Then just use scalling of AO using /tf/WW/en/Posts/31698#top). My suggestion is use AO there like a speed setpoint and another DOs like enable. start and stop signals to the drive. According to the type of drive you can find in thier manuals how to assign and hardware connect external signals. Best regards, Hristo Mihalev |
Follow us on