Hi there, I'm working on a Tia Portal V16 Upd4 project with a UPS1600 + UPS1100 battery 3,2 Ah, a PC/soft PLC CPU 1515SP (V21.8) all connected trough Profinet with XC-206-2. When I go to Online in hardware view with UPS1600, there is a red maintenance key on UPS1600 and all subordinate elements are OK in green. I don't know where is the problem, in diagnostic view the information it's not very clear. In attached zip file you can see several screenshots with hardware view online, diagnostic buffer, alarm view on WinCC, etc. In my first download to plc, I select V2.4 firmware for UPS1600, but when I check my hardware I saw that it was V2.3, then I change in Tia to V2.3, compile all hardware and download again but the error is the same. Maybe a SITOP UPS1600 firmware update V2.4 could solve the problem, but I can't find a download link in this forum. Thanks in advance Litos97 AttachmentUPS1600_ERROR.zip (509 Downloads) |
6/5/2021 11:20 AM | |
Joined: 9/21/2012 Last visit: 9/18/2024 Posts: 4141 Rating: (463) |
And what do you find in the PLC diagnostics buffer? |
6/5/2021 2:41 PM | |
Joined: 9/27/2006 Last visit: 9/18/2024 Posts: 12282 Rating: (2684) |
Hello litos; It could very well be a firmware version incompatinbility. Here is a page from the UPS1600 manual showing how you can determine what version you have presently (see the screenshot below) anf a download of firmware version 2.3, the latest available: - Sitop UPS1600/UPS1100 manual: https://support.industry.siemens.com/cs/ww/en/view/84977415 - Firmware for Uninterruptable Power Supply SITOP UPS1600 https://support.industry.siemens.com/cs/ww/en/view/79207181 Hope this helps, Daniel Chartier |
6/9/2021 6:33 PM | |
Joined: 9/28/2008 Last visit: 9/16/2024 Posts: 14 Rating: (0) |
Hi Daniel, Thanks for your information!! I check the firmware version offline and online several times and they are the same. This morning I overwrite the same firmware version V2.3 and nothing changes. Today I've received 6 new units of UPS1600 from Siemens and the same problem occurs. I've tried with new version Tia Portal V17, and nothing new, when I´m going trough diagnostic buffer PLC I see an error in a subordinate element called "Config submodule" as you can see in attached zip file. This file has several screen shoots from plc diagnostic buffer. Thanks in advance Litos97 AttachmentPLC_buffer_diagnostic.zip (525 Downloads) |
6/11/2021 12:02 PM | |
Joined: 9/28/2008 Last visit: 9/16/2024 Posts: 14 Rating: (0) |
Thanks you Georg, I´ve deleted profinet links in topology view, compile all and downloaded to PLC, but the situation is the same. In diagnostic buffer I can see an icon with 0101 at Config Submodule as you can see in attached file. The explanation info about this module icon with 0101 says something about updating input / output image access error ¿? Thanks Litos97 AttachmentSubmoduleIOerror.zip (452 Downloads) |