I have often found changes in the process piping cause backflow, flow when previously there was no flow or stopped flow when the should be flow. Just because if was one way last week, doesn't always mean it's the same way this week. When troubleshooting a false flow indication, check the the troubleshooting section of the Mag 5000/6000 manual. It shows that an electrode cable bad connection, missing connection or damage to the shielding of the electrode cable can cause false flow indication.
|
Last edited by: danw at: 2/21/2017 1:48:58 AMLast edited by: danw at: 2/21/2017 1:49:13 AM |
|
4/1/2017 5:57 PM | |
Posts: 1 Rating:
|
Hi both, We have same problem with a MAG 5000: negative flow readings. I can´t see the pics in the last post. Could u repost it in other server? Thank you. Cheers |