6/11/2015 3:15 PM | |
Joined: 8/31/2005 Last visit: 8/20/2024 Posts: 2198 Rating: (328) |
After reading the manual (https://support.industry.siemens.com/cs/ww/en/view/107623221, Chapters A.7.2 and A.7.3, I say: The suffix "L" is the common contact, "X" the normally closed contact and "" the normally opened contact. So you have to use "L" and "" as switch. Your pump will run when the DQ is set to true. The "a" is the byte address of your output. It is defined when in TIA Portal in "Devices & Networks" and 0 to 7 are the bit address of your output. Of you are using DQa.0 you should connect your 24C from the power supply to Pin 5 and your pump to Pin 7 and 0V from the power supply.
AttachmentPages from s71200_system_manual_en-US_en-US.pdf (207 Downloads) |
|
|