hello, i have installed a 75kw soft starter in a pump application my problem is that i don't have soft stop I'm using 3RW40 |
10/1/2007 2:51 PM | |
Posts: 23 Rating: (3) |
Hello
well I'm setting a ramp 10 sec but the pump stops imidiately |
10/9/2007 1:31 PM | |
Posts: 25 Rating: (2) |
Hello, for a soft stop ramp at the 3RW40 you have to parameterize the ON/ RUN contact as follow. How to parametrize the ON / RUN contact 13/14 of SIRIUS Softstarter 3RW40: |
10/9/2007 1:53 PM | |
Posts: 23 Rating: (3) |
thank you very mach i'll try it |