4/24/2010 6:40 AM | |
Joined: 10/7/2005 Last visit: 10/4/2024 Posts: 3024 Rating: (1054)
|
Hello Hike Iwonder if you "forgot" to delete DB1, 2 & 3 (DB_WORK_NO, DB_SEND_NO and DB_RCV_NO) online in the PLC when you changed FC100 (SWR_START) parameters (this would explain the problem that you are having). Have a look at chapter 5.8 of THIS manual for more info on this matter. The other thing tolook out for is thatthe new DB's must obviously not only exist in the PLC but also be contiguosly allocacted as ofthe "DB_NO" value of FC100. I hope this helps |
Cheers |
|
4/25/2010 8:02 PM | |
Joined: 7/2/2008 Last visit: 9/30/2024 Posts: 928 Rating: (308)
|
Hello Hike,
I wouldn't write better than fritz. Just 2 little things, 1-Make surethat the length of each data blockis more than 2 words (Check this FAQ). 2- What I'm going to say is not related to the problem but I recommend to download OB121 and all error OBs as well to avoid the STOP mode in future. Best regards. H-H |
This contribution was helpful to2 thankful Users |
5/8/2010 9:28 PM | |
Posts: 138 Rating: (0) |
Thanks both of you. Infact the problem were both of them mentioned in the replies. Thanks again. |
This contribution was helpful to2 thankful Users |