Industry Online Support
Technical Forum
8/28/2013 11:23 AM | |
Joined: 8/19/2013 Last visit: 3/6/2024 Posts: 148 Rating: (10) |
Hi Niklas depending on the type ofmodule you can only switch offthe short circuit testfor the entire module or for a group. So it is not possible to separate the channels for that functionality ! Nextstep is, you have to set up the right parameters like evaluation 1oo1 only a single channel sensor is connected 1oo2a two channel sensor is connected - equivalent means both channels from the sensor are from the same typ NC! if not you will get a fault - non - equivalent means the channels are different -> 1 NC 1 NO then it is a must that you cpnnect the NC to channel1 and the NO to the 2nd channel !! If you set up non- equivalent it is anecessary that you have the right order Pls have look to the manual http://support.automation.siemens.com/WW/view/de/34474892 Chapter 7.5.7 Regards ! |