11/5/2016 11:02 AM | |
Joined: 12/18/2014 Last visit: 11/13/2024 Posts: 34210 Rating: (4261)
|
What color should the display show by day? White or amber? |
11/5/2016 11:50 AM | |
Joined: 12/18/2014 Last visit: 11/13/2024 Posts: 34210 Rating: (4261)
|
I took the color white by day. The error in the setpoint switching has resulted from your program change with the color markers. AttachmentVarmestyring_V5_Final.zip (377 Downloads) |
Last edited by: ixo65 at: 11/5/2016 11:51:35 AM |
|
This contribution was helpful to1 thankful Users |
11/5/2016 9:20 PM | |
Joined: 12/18/2014 Last visit: 11/13/2024 Posts: 34210 Rating: (4261)
|
I have revised the program again and the setpoint processing from individual blocks converted to UDFs. This makes the whole thing even clearer.
AttachmentVarmestyring_V6_Final.zip (404 Downloads) |
This contribution was helpful to1 thankful Users |
11/6/2016 7:53 AM | |
Posts: 67 Rating: (7) |
Doh, what a bummer I have set a max at 25 C, if a switch should get stuck (unlikely, but anyway) Also the day program should be activated when I5 is high. I think this should work. For translation: Dag = Day, Nat = Night For rev. 6, i can't find the upper limits, nor the hysteresis adjustment. AttachmentVarmestyring_V5_1_Final.zip (370 Downloads) |
11/6/2016 8:31 AM | |
Joined: 12/18/2014 Last visit: 11/13/2024 Posts: 34210 Rating: (4261)
|
For V6.1: A double click on the UDF opens the parameter list.
AttachmentVarmestyring_V6.1_Final.zip (362 Downloads) |
This contribution was helpful to1 thankful Users |
11/6/2016 8:42 AM | |
Posts: 67 Rating: (7) |
Thanks, that makes sense.. I'll give, it's a lot cleaner that way. |
This contribution was helpful to1 thankful Users |
11/6/2016 9:22 AM | |
Posts: 67 Rating: (7) |
So, just have to wire it up.. How much ventilation do I need to make in the box? AttachmentPhotos.zip (371 Downloads) |
11/6/2016 9:36 AM | |
Posts: 67 Rating: (7) |
So ie. one ø40 mm hole with a filter in top and bottom should be enough. There should be some natural flow i guess. |
11/12/2016 10:07 AM | |
Posts: 67 Rating: (7) |
Finally my Siemens QAA2061 arrived - It's all up and running. It works like a charm. I've played around, added a VFD output for fan control. Also some counters. (Haven't tested it yet) Is it possible to automatic update the reset date on display 2? AttachmentVarmestyring_V6.2_Final.lsc.zip (401 Downloads) |