Hi sergio, i got almost the same problem I am working on one old machine, and the pc that manager everything is died..... Now i am trying to start the hmi from my pc in runtime (is the first time that i use wincc6.2, i believe is more old of me ......) anyway also if a change the name like the link that someone posted is not working the error is alwais the same """the project cant start because the pc is not registrated on the server""" Did you find some solution?? i hope that you can help me Thanks ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 09/17/2021 09:16:23New subject after splitting |
|
9/17/2021 8:27 AM | |
Joined: 5/16/2014 Last visit: 9/12/2022 Posts: 7298 Rating: (2167)
|
Hello ton-io10, the name of the local computer need to be set as "Server" If you have set the local computername as "Server", see FAQ: https://support.industry.siemens.com/cs/ww/en/view/109779249 Regards Georg Berghof |