I found this link which may be of some assistance: Contact | Building technology | Siemens Global You want to mix building automation with industrial automation, both Siemens systems. Makes perfect sense they should be able to share data. Unfortunately this is the Portal group, not the DESIGO CC group (conference). If you know what data you need and what format it is needed, and a common communication method both systems can effectively work together through, tell us here and maybe we can suggest options.
|
science guy |
|
9/7/2021 7:23 PM | |
Joined: 11/8/2017 Last visit: 7/16/2024 Posts: 328 Rating: (180) |
Hi, See HERE for more information. This is located in the Desigo section of the forums. Also refer to the attached file from the Desigo CC help files - I'm not familiar with the S7 hardware / engineering processes, so hopefully this of some use to you as a starting point. Regards, |
Last edited by: _CJ at: 09/08/2021 18:18:29 |
|
This contribution was helpful to1 thankful Users |
9/7/2021 7:55 PM | |
Joined: 11/8/2017 Last visit: 7/16/2024 Posts: 328 Rating: (180) |
Hi, Ok, an update: The creation of the CSV file is a manual process. See HERE. The CSV requirements are described in good detail. Note the reference to a template CSV file being available with the Desigo CC installation - I would suggest you start with this. The link above comes from the 'Engineering Reference' section of the Desigo CC help. There's more information on the integration requirements under the 'Engineering Step-by-Step' section in the Table of Contents. Regards, |
This contribution was helpful to2 thankful Users |