10/15/2018 3:30 PM | |
Joined: 9/23/2005 Last visit: 6/9/2023 Posts: 4184 Rating:
Hi, I posted here a sample project with calibration blocks (without and with 1 weight) for ET200SP AI 2xSG 4,6-wire HS module (TIA V15). There are also user data types to the inputs / outputs to normal / isochronous operation. Some additional tips, from product manual: Because the filter also filters for a multiple of 50/60 Hz, it may be better to disable the filter. Any setting values is scaled to +/- 100,000,000 digits in the module. Prefilter "Input lock B": This is a moving average value filter which prefilters the signal when it exits "Input lock B" mode.AttachmentForceCalibration.zip (153 Downloads) |
Denilson Pegaia |
This contribution was helpful to
3 thankful Users |
10/17/2018 11:52 AM | |
Hi, this program version include also an two weight calibration. AttachmentForceCalibration.zip (149 Downloads) |
Denilson Pegaia |