3/25/2013 12:55 PM | |
Joined: 9/23/2005 Last visit: 2/3/2023 Posts: 4178 Rating:
Hi, Despite of it is pretty simple; here there is a sample project that exemplifies the use of diagnostic memories. The project has two analogical modules, once in the central rack, the other one in the ET200MP. In the Modules Properties (Device View), I set the diagnose bit function (Module Parameters -> Value status). Optionally, I set all diagnose possibility for the first channel too (Module Parameters -> AI8->Inputs-> Channel0). The analogical values (and the diagnostic bits) could be showed at the Watch Table. An primitive example of use of the diagnostic bit is showed on the OB1. AttachmentDIAG_BitDiag.zip (397 Downloads) |
7/24/2016 9:06 PM | |
Posts: 5225 Rating:
Hi Greg, Please see the attached PDF with some hints on how the configuration of the original example works. See if helps... otherwise give the guys a sample project to work from with your application problem. Cheers. AttachmentVisual clue_Diagnostic bits.pdf (244 Downloads) |