Hi, As from TIA V17 it is possible to work with a WinCC Unified as OPC UA client for data acquisition (DA), both, in Runtime and HMI. Now, it is also possible to use signed and encrypted communication and authentication (user and password) of client HMI. Configuration steps: To set the connections:
TIP: There are the follow options to access (Sign means data packets are signed with the certificates but not encrypted; SignAndEncrypt means data packets are signed and encrypted with the certificates):
To tag configuration:
For Certificate handling: If you set something different as none for “Security Policy” and ‘Message security’, it would be necessary to work with certificates. TIP:
Main steps:
For the first engineering station /client’s access to the PC Runtime the steps are:
TIP:
|
Denilson Pegaia |
|
This contribution was helpful to
3 thankful Users |
1/12/2022 12:49 PM | |
Joined: 7/9/2019 Last visit: 5/1/2024 Posts: 14 Rating:
|
Denilson, is this available on TIA V16 Unified PC RT? |
1/13/2022 11:15 AM | |
Joined: 9/23/2005 Last visit: 3/24/2025 Posts: 4406 Rating:
|
Hi, The OPC UA Channel exists also in WinCC Unified V16, however it was publish as a feature just as from TIA V17 Delivery release ( https://support.industry.siemens.com/cs/br/en/view/109792165 ). |
Denilson Pegaia |
|
10/11/2023 6:00 PM | |
Joined: 12/14/2022 Last visit: 1/16/2025 Posts: 78 Rating:
|
Hi, even with OPC communication my minimum Aquisition cycle is 100ms? |