12/14/2012 6:08 PM | |
Joined: 4/22/2010 Last visit: 10/17/2024 Posts: 5697 Rating: (715)
|
Hello, in short: A transistor output can switch max. 0.3A, a relais output can switch up to 10A. That's the biggest difference. So you can say you use transistor output for small loads 24V (or 12) and you use relais outputs for heavy loads or loads wich must be swiched potential free. you can have a look at the logo Manual For more technical details. regards, Marcjan |
Last edited by: Marcjan at: 12/14/2012 6:12 PMProblem solved? |
|
This contribution was helpful to2 thankful Users |
12/14/2012 6:14 PM | |
Joined: 8/16/2010 Last visit: 11/5/2024 Posts: 638 Rating: (12) |
Ok... So I can use transistor outputs to control relay coil (A1,A2), or directly use PLC with relay outputs. |
12/15/2012 9:35 AM | |
Joined: 8/16/2010 Last visit: 11/5/2024 Posts: 638 Rating: (12) |
Thanks. You realy helped me- Best regards, Miloš |
6/13/2013 8:14 AM | |
Joined: 4/22/2010 Last visit: 10/17/2024 Posts: 5697 Rating: (715)
|
Hello, It's in the manual, but maybe not that clear. The specs off the relais is the same as for the 230V version. The Max load depends on the type of load. Attached you find the specs. regards, Marcjan Attachmentlogo230-v.pdf (754 Downloads) |
Last edited by: Marcjan at: 6/13/2013 11:47 AMProblem solved? |
|
6/13/2013 11:39 AM | |
Posts: 7 Rating: (0) |
Marcjan , thanks ! So there is no worries to connect coil of contactor to 220v thanks again |
This contribution was helpful to1 thankful Users |
Follow us on