10/10/2012 1:34 PM | |
Joined: 9/27/2006 Last visit: 1/15/2025 Posts: 12328 Rating: (2698)
|
Hello mahmoud; The easieast (and cheapest) way to expand the S7-300 rack is with a IM 365 : http://support.automation.siemens.com/WW/view/en/4068543 You will find further descriptions on the IM 365 in the S7-300 module data manual, in the chapter on Interface Modules: SIMATIC S7-300 S7-300 Automation System Module Data Hope this helps, Daniel Chartier Edit: Darius is correct, the CPU 312 iss limited to only one rack, and it cannont use the IM 365 or IM 360/361 pairs. See the attached document, from the S7-300 CPUs technical specifications manual |
Last edited by: dchartier at: 10/10/2012 1:43 PMOups, Darius caught me! |
|
This contribution was helpful to1 thankful Users |
10/10/2012 2:50 PM | |
Joined: 10/7/2005 Last visit: 1/15/2025 Posts: 3029 Rating: (1058)
|
You could also add a CP342-5 and ET200M to your 312CPU as additional I/O station. I hope this helps
|
Cheers |
|
This contribution was helpful to2 thankful Users |