6/25/2019 4:02 PM | |
Joined: 12/18/2014 Last visit: 8/6/2024 Posts: 33498 Rating:
|
Yes , it's possible. You can set the LOGO! as client and the S7 as a server. |
6/25/2019 11:35 PM | |
Joined: 9/7/2010 Last visit: 7/22/2024 Posts: 50 Rating:
|
Thank You. I will give it a go ! |
6/27/2019 2:35 PM | |
Joined: 12/18/2014 Last visit: 8/6/2024 Posts: 33498 Rating:
|
In attachment an example. TIA V14 SP1 Update 7; S7-1212C; LSC V8.2.1; LOGO! 8.FS4. To be able to test the example in reality, I unfortunately had to use a 1212C as an S7 CPU, because I have one. The LOGO!, which I have, is a LOGO!8.2 12/24 RCE. The most important: Set up a network project in the LOGO! program. Insert a LOGO!8.FS4 and an S7-compatible device there. Create an S7 connection between the LOGO! and the S7 (with the LOGO! as client), in which you pull the connection line from the LOGO! to the S7.
Attachmentprovence.zip (239 Downloads) |
This contribution was helpful to
1 thankful Users |
7/1/2019 1:46 AM | |
Joined: 9/7/2010 Last visit: 7/22/2024 Posts: 50 Rating:
|
Thank You For this. |
This contribution was helpful to
1 thankful Users |
Follow us on