Hello balachandar Configure a drive in PROFINET is quite easy; basically you have to assign the IP address, assign the name and choose the telegram. Also you have to configure the same telegram in the drive in P0922 P0922 - Selects the PROFIdrive Standard Telegram. Value: 1: Standard Telegram 1 20: Standard Telegram 20 350: Standard Telegram 350 352: Standard Telegram 352 353: Standard Telegram 353 354: Standard Telegram 354 Attached is an excerpt of how to configure the drive. You can see also al example: SINAMICS G120 with CU240S PN (FW3.2): Control via PROFINET http://support.automation.siemens.com/WW/view/en/45287261 I hope this help!!! AFP AttachmentS7-300 - PROFINET - CU240S-PN.pdf (780 Downloads) |