Joined: 3/14/2008 Last visit: 11/16/2024 Posts: 2131 Rating: (953) |
Hello Berg, Yes, this is possible. In order to use this, you have to set FeatureBit3 to "1": Enabling resetting of commands for the control settings. You can interconnect a digital input to the control buttons, when the digital signal is "0", the control settings are automatically reset. But... you can also take a look at FeatureBit4: "0 = Button mode; 1 = Switch mode". In case of a VlvL, you can use OpenAut to open the valve. When the OpenAut is "0", the valve closes again. You will not have to use CloseAut when the FeatureBit4 is set to "1". See attachments (in this post and next post) Attachmentmk_@MSITStore_C__Program%20Files%20(x86)_SIEMENS_STEP7_s7li222bs_P.pdf (72 Downloads) |
Last edited by: Oreca at: 4/25/2016 7:07:18 PMIf I could help you, you can use the RATE button. Thank you. |
|