4/9/2016 9:26 PM | |
Posts: 1 Rating:
|
Hello I want a card (wago 750-333) Network (Profi Bus) I connected. File (gsd) I installed and configured the way I did view Tips (wago) Please advise why software (Simatic manager 5.5) embraces this card? Following the application file and I send some photos. CPU used (s7-300 313c2dp) Thank you for your cooperation ------------------------------------------------------------------------------------------ |
Last edited by: Blue Moderator at: 4/10/2016 9:51:32 PMNew subject after splitting |
|
4/9/2016 9:40 PM | |
Joined: 3/28/2015 Last visit: 9/30/2023 Posts: 716 Rating:
|
Hello, Kindly find the attached file. AttachmentConfiguration a Profibus-DP node using Step7 and WAGO_IO.pdf (501 Downloads) |
Eng.Mohamed Ibrahim |
|
This contribution was helpful to
1 thankful Users |
4/15/2016 8:35 AM | |
Joined: 11/18/2010 Last visit: 8/5/2022 Posts: 523 Rating:
|
it looks from your attached image you have inserted wrong DP slave device ,first confirm which FW of wago you are looking for .please refer attachment it should look like that in HW Config window. viral patel |