8/17/2021 7:42 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, Welcome to forum. Please open new topic instead of posting your query in old topic. Here I prsume contactor damages power contacts. How is field contactors control operation? Is field contactor logic is controlled via drive or it is externally interlocked? Please refer attached sheet which shall help you to wire field reversal contactor control wiring & shall help you to set related parameters. If it is externally, please check if you have wired aux NC contacts of both the contactors in control logic, which will ensure operation of second contactor only when first one is switched OFF state. Check an appropriate value of varistor is connected across field winding. You can calaculate the value of varistor refering formula explained in attached sheet. HTH AttachmentDCM field reversal logic.pdf (413 Downloads) |
8/22/2021 11:02 AM | |
Posts: 9 Rating: (0) |
THANKS FOR YOUR REPLY. THIS IS THE CONTROL CIRCUIT OF CONTACTOR: WHAT HAPPEN IF USE AC CONTACTOR? |
Last edited by: ebrahimsaadati at: 02/13/2022 08:48:53 |
|
8/23/2021 5:56 PM | |
Joined: 7/7/2010 Last visit: 10/18/2024 Posts: 15327 Rating: (2432) |
What speed is the motor rotating when the contactor toggles forward/reverse? If the answer is not 0, that's the problem. When the motor is at 0 rpm for a short period of time, it is electrically safe to toggle the direction contactor. Are you using the drive to manage the contactor? If not, consider changing the motor drive configuration so it handles the direction change from an external digital input.
|
science guy |
|
This contribution was helpful to1 thankful Users |
Follow us on