8/14/2014 5:44 AM | |
Joined: 11/21/2007 Last visit: 9/25/2024 Posts: 2325 Rating: (308) |
Hello As per the product information of latest DIGSI 4 version V4,89 ( Attached ) the compatible versions are : a)DIGSI 4 V4.85 / V4.86-> STEP7 V5.5+SP1 b) DIGSI 4 V4.87 / V4.88 / V4.89 -> STEP7 V5.5+SP2 Curiously ( It does not mention "and higher" ). So there is no clear confirmation that STEP7 5.5 SP4 is compatible with any DIGSI version. You have 2 options : a) Check with energy support : energy.support@siemensand ask for a confirmation b) Downgrade your STEP7 installation to V5.5 + SP1 for your existing DIGSI version. or to SP2 for the latest DIGSI version Hope this helps Cheers Navnag AttachmentProduct_Information_DIGSI4_V4_89.pdf (700 Downloads) |
There is no such thing as the last bug in a program |
|
8/14/2014 8:07 AM | |
Joined: 3/21/2006 Last visit: 10/4/2024 Posts: 10229 Rating: (1181) |
DIGSI 5 |
8/14/2014 11:29 AM | |
Joined: 11/21/2007 Last visit: 9/25/2024 Posts: 2325 Rating: (308) |
As per the Siemens Energy Website , : DIGSI 4 is required for SIPROTEC-4 relays and DIGSI 5 is required for SIPROTEC-5 relays. I am not sure, but I think DIGSI-4 and DIGSI-5 ( I have not used DIGSI-5 yet ) are two different softwares with different capabilities. DIGSI 5 does not replace DIGSI-4. Cheers Navnag |
Last edited by: Navnag at: 8/14/2014 11:29 AMThere is no such thing as the last bug in a program |
|
8/15/2014 11:49 AM | |
Joined: 10/9/2007 Last visit: 10/4/2024 Posts: 1250 Rating: (115)
|
|
Energy Automation products: Sicam, Siprotec, Digsi |
|