Hello, I want to get some parameters from Yaskawa V1000 drive to my PLC (314C-2 PN/DP). I have installed successfully the GSDML file in hardware configuration. Using the drive software (DriveWizard), I can see the parameters (reference frequency and output frequency). But when I try to monitor these parameters in Step 7, no value is displayed. Here (page 29) you can find the drive's profinet I/O modules. Attached you can see a screenshot of drive's online module. I've tried to use the other two modules (IO40 Profile or Std Tgm+5PZD), but the result is the same. I also have tried to use an older version of the gsdml, but with no result. What should I do in order to get the parameters'value in my PLC? Many thanks in advance! |
5/24/2019 2:49 PM | |
Posts: 2826 Rating: (684) |
Hello. There is no PIW/PQW to read-from/write-to for communication linked partners. Please use plainly IW/QW. BR |