10/27/2022 7:06 AM | |
Joined: 12/22/2016 Last visit: 9/18/2024 Posts: 4 Rating: (1) |
Dear All, I am struggling with configuring communication between Open Controller and WinCC Unified on different computers (routing through Windows System) and I am looking for help. I followed the manuals and still the WinCC Unified PC cannot access the PLC. Setup: 1. Host:
2. Open Controller:
3. WinCC Unified PC:
I can load both Open Controller and WinCC Unified PC from TIA Portal, but I cannot ping Profinet port "Software_PLC" X1 192.168.1.1. I tested all possible PG/PC interfaces with no effect. Please find screenshots of the configuration in the link: [snip] Thank you, Piotr AttachmentOpenControllerWinCCUnified-20221027T101220Z-001.zip (408 Downloads) |
Last edited by: Jen_Moderator at: 10/27/2022 10:13:15Link removed and file attached. |
|
10/27/2022 10:41 AM | |
Joined: 1/21/2013 Last visit: 11/11/2024 Posts: 3253 Rating: (506) |
Hi Piotr, to me it looks like you are using a SIMATIC BusAdapter without RJ45 connector or you forgot to order a SIMATIC BusAdapter. Kind regards |
10/27/2022 1:13 PM | |
Joined: 12/22/2016 Last visit: 9/18/2024 Posts: 4 Rating: (1) |
Stefan, manual is attached. Best, Piotr EDIT: I ordered a bus adapter and should receive it next week. Hope it will solve all communication problems. EDIT2: The bus adapter fixed everything and now it works. But by looking at the manual, it should be possible to configure it on one port only :) Best, Piotr AttachmentSoftwareController_WinCCUnified_V17.pdf (393 Downloads) |
Last edited by: kukifas2 at: 10/28/2022 08:02:20Last edited by: kukifas2 at: 11/08/2022 08:11:37 |
|
This contribution was helpful to2 thankful Users |