Joined: 10/1/2013 Last visit: 5/8/2024 Posts: 605 Rating: (71)
|
Hi Ipermix, first of all I need to know the order number of your RF310R to answer your questions (6GT2801-xxxxx). |
7/9/2019 7:01 PM | |
Joined: 10/1/2013 Last visit: 5/8/2024 Posts: 605 Rating: (71)
|
Every command function block (read, write, etc..) has error and status outputs. So you have to evaluate those outputs. Additionally there's a block called "Reader-Status". Check out it's description here (chapter 10.2.1): That's all the options you have for diagnostics. Usually the err LEDs start to flash only after you submitted a command. So check the outputs of the corresponding block (read, write, etc...). Please don't use FC/FB45 in TIA V14. Those blocks won't make you happy |