7/5/2019 11:42 AM | |
Joined: 6/1/2018 Last visit: 10/27/2022 Posts: 18 Rating:
|
Sorry I have a news. For more details I have write a file with all information. Tanks for your help Marco AttachmentDocumento Richiesa Aiuto OnLine_EN.pdf (351 Downloads) |
Last edited by: Jen_Moderator at: 07/09/2019 06:06:09New subject after splitting Last edited by: Jen_Moderator at: 07/09/2019 06:13:36Removed splitting-remark. |
|
7/9/2019 11:34 AM | |
Joined: 10/1/2013 Last visit: 5/11/2023 Posts: 604 Rating:
|
Hi Ipermix, first of all I need to know the order number of your RF310R to answer your questions (6GT2801-xxxxx). |
7/9/2019 7:01 PM | |
Joined: 10/1/2013 Last visit: 5/11/2023 Posts: 604 Rating:
|
Every command function block (read, write, etc..) has error and status outputs. So you have to evaluate those outputs. Additionally there's a block called "Reader-Status". Check out it's description here (chapter 10.2.1): That's all the options you have for diagnostics. Usually the err LEDs start to flash only after you submitted a command. So check the outputs of the corresponding block (read, write, etc...). Please don't use FC/FB45 in TIA V14. Those blocks won't make you happy |
7/11/2019 8:36 AM | |
Joined: 6/1/2018 Last visit: 10/27/2022 Posts: 18 Rating:
|
Hi Owei AttachmentPicture for Owei.pdf (305 Downloads) |
Last edited by: Jen_Moderator at: 07/11/2019 09:32:59Edited text for better reading. |
|
Follow us on