Hello alexfizeau, You have made anarea pointer for the alarm messages. When a bitis set in PLC, the coresponding message will be shown. When you acknowledge the alarm, the bit in PLC stays set. The alarm is still there, but you acknowledge that you have noticed it. The PLC programm has to reset that bit, when that alarm isn't present anymore. Here is a link for manual OP7: http://support.automation.siemens.com/WW/view/en/1145112 And a manual for communications: http://support.automation.siemens.com/WW/view/en/1137086 Best regards, Wizard |