11/1/2020 5:54 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, If you have connected all thermocouples as analog input, then you need to set correct input type, measuring range in module hardware configuration. Also check if you have set correct measuring position on your analog module, in your case A, of all channels of analog module since you have connected thermocouples. Please refer SIMATIC S7-300 SM331; AI 8 x 12 Bit Getting Started part 3: Thermocouples for detail information about setting of measuring position on module, hardware configuration & electrical connection of thermocuples. HTH |
Last edited by: PISCEAN 2010 at: 11/01/2020 07:04:58Last edited by: Jen_Moderator at: 11/02/2020 09:51:49Optimized link. |
|
11/1/2020 2:52 PM | |
Joined: 10/24/2013 Last visit: 10/10/2024 Posts: 46 Rating: (0) |
hi the sensor is pressure transducer 0-33mv output |
11/1/2020 2:53 PM | |
Joined: 9/27/2006 Last visit: 10/13/2024 Posts: 12287 Rating: (2685)
|
Hello plc_lover; What about the other information requested? Daniel Chartier |
11/1/2020 3:10 PM | |
Joined: 10/24/2013 Last visit: 10/10/2024 Posts: 46 Rating: (0) |
hi the channels is A position the sensor is connected to plc through pin 12,13 |
11/3/2020 9:22 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, Can you attach snap shot or electrical wiring schemetic of SM331 analog input module here? as per expert memberdchartier's earlier post. |