4/30/2019 3:47 PM | |
Joined: 9/27/2006 Last visit: 6/7/2024 Posts: 12260 Rating: (2670) |
Hello rotsen; This might be the replacement Siemens MLFB you are looking for: 6ES7655-5DX60-1BB0. An optinal link: In many of our projects we used Fieldbus Foundation distribution blocks from MTS, now a property of Relcom: http://relcominc.com/fieldbus/fcs-mb.htm These Megablocks allowed us to create distribution points (chicken-feet) of different number of connections, by combing blocks of various sizes (2,4, 8, 10 or 12 instrument drops).They worked very well, offered add-on termination blocks and integrated short-circuit protection (SpurGuard) at every junction. We had very good results with them. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 04/30/2019 15:56:50 |
|
5/1/2019 4:51 PM | |
Joined: 9/27/2006 Last visit: 6/7/2024 Posts: 12260 Rating: (2670) |
Hello rotsen; It took me a bit of time to find out, first, that you were right about the cancellation of the AFS and then to understand why no replacement/successor module was available. It seems that redundancy of the H1 bus is done now exclusively through 2 redundant Compact FF Links (mounted on a redundancy bus module), in a ring configuration with either an AFD or AFDISD. See the following screenshot, where the illustrations are taken from the PCS 7 Catalog, 2019 version (chapter 10). Catalog ST PCS 7 (system components) SIMATIC PCS 7 for V9.0 https://support.industry.siemens.com/cs/us/en/view/109745632 The manual for the Compact FF link and redundancy bus module can be found here: SIMATIC Bus link Compact FF Link https://support.industry.siemens.com/cs/us/en/view/109739578 If any doubts persist, I would suggest you contact either a Siemens tech (though a Support Request, the link can be found at the top of this page) or your nearest Siemens rep. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 05/01/2019 16:52:50Last edited by: dchartier at: 05/01/2019 17:05:39 |
|
This contribution was helpful to1 thankful Users |
Follow us on