HI, THE PLC IS S71200 CPU1214 DC/DC/DC with ET 200 SP, AQ 4XU/I and HMI KTP600 BASICCOLOR PN |
5/8/2015 8:13 AM | |
Joined: 2/19/2013 Last visit: 5/23/2024 Posts: 184 Rating:
|
You have to use NORM_X and SCALE_X instructions on the PLC side. |