8/7/2009 5:07 PM | |
Joined: 8/31/2005 Last visit: 1/20/2025 Posts: 2198 Rating: (330)
|
As far as I know there is only one (actual) F-AI module. You can connect 2 or 4 wire sensors. Look into the manual or into this application. |
Last edited by: miami at: 8/7/2009 5:08 PM |
|
8/8/2009 2:13 PM | |
Joined: 10/7/2005 Last visit: 2/6/2025 Posts: 3033 Rating: (1060) |
Hello Arpit your questions are of a very generic nature (nothing wrong with that), but there are unfortunately no simple (generic) answers tothem. It does depend on thetype of Instrument you use (e.g. isolated versus non-isolated) and to a lesser extend to the type of chosen AI card. Anyway, miami already supplied with you info/links about F-AI's so I'll just add a few hopefully useful links for "normal" AI's: Please note that all these links relate to S7-300 (ET200M) type AI's, if you want to use ET200S or S7-400's AI's etc. etc. you'll find similar connection info in their manuals too. S7-300 I/O Analog --Connecting and wiring modules SM331 AI 8x12 Bit Getting Started guide part 1: 4 -20mA SM331 AI 8x12 Bit Getting Started guide Part 2: Voltage and PT100 SM331 AI 8 x 12 Bit Getting Started guide part 3: Thermocouples SIMATIC S7-300 S7-300 Module data(see especially chapter 4) I hope this helps (and don't know why I can't untick BOLD anymore) |
Last edited by: fritz at: 8/10/2009 1:52 AMCheers |
|
This contribution was helpful to2 thankful Users |
8/11/2009 9:01 AM | |
Posts: 49 Rating: (1) |
THANKS IT HELPED ME A LOT.... |