Industry Online Support
5/13/2011 5:04 PM | |
Joined: 9/27/2006 Last visit: 7/20/2024 Posts: 12270 Rating:
Hello Arif; Is the ION software designed as a Modbus master (I do not know this system and might ask unseemly questions, but this is the kind of detail that is important). If so, what Modbus codes does it support? What type of communication interface does it require (and does the Sentron support the same, RS-232, RS-485...)? How is the Sentron Modbus slave interface setup (address, baud rate, parity...)? Here is a link to the Modbus communications manual for the Sentron 3WL. Please locate the ACB status you want to read in the Modbuis data map you will find there, so we can help you request it from your Modbus master. https://a248.e.akamai.net/cache.automation.siemens.com/dnl_iis/zE/zE1Njc4NwAA_39850157_HB/SENTRON_WL_VL_circuit_breakers_with_communication_capability_MODBUS_EN_en-US.pdf Hope this helps, Daniel Chartier |
2/6/2013 2:02 PM | |
Hello msalomone; See if chapter 6 in the following manual provides the information you need: System Manual SENTRON 3WL/3VL Circuit breaker Remember that data exchanges allowed with the Sentron 3WL depend on the "Basic Type" selected. Hope this helps, Daniel Chartier |
