Thanks. I received GSD file from ABB and I installed it. While doing the configuration I noticed that We are having problem with the addressing of the ABB Modules with Siemens Ladder Logic. E.g The Input Module selected in the H/W is a 16 ch Input Module but it occupies 4 bytes. Also see attached the configuration is in BYTE than what we normally do in siemens is BIT. How can we configure this in logic ? is it IB or PIB for digital input read ? Attachmentabb.zip (720 Downloads) |
9/17/2008 2:02 PM | |
Posts: 162 Rating: (23) |
Hi Rajendra, although 4 bytes inputs must be forgiven if only two exist, on can read only two, but then directly (I10.0; I10.1; etc). Best regards FrankW |
10/26/2009 9:40 PM | |
Joined: 5/28/2008 Last visit: 10/7/2024 Posts: 4515 Rating: (839) |
Dear Rajendra, Open HW config. and right click on the row of "DI801" and select edit symbols. A pop up window will appear with symbols and addresses of inputs. You can also put here the symbols of the addresses. Regards, |
Ayman Elotaify |
|