12/22/2011 1:36 AM | |
Joined: 9/27/2006 Last visit: 10/15/2024 Posts: 12289 Rating: (2686)
|
Hello Martins; 2 things I notice in your jpg: - you have set the Bipolar parameter to 1, which makes the FC105 expoect an input value (from PIW438) to be in a range of -27648 to +27648, Since your LO_Limit is 0.0, I would use a FALSE (or 0) value for Bipolar, -The input signal is presently higher than the standard expected range (a decimal value of 27648 for a PIWxxx address) so the output value is clamped at Hi_Limit, your HI_Limit parameteris setat 497.0 and your output is 497.0 What were you expecting different? What uis the maximum flow you expect your flowmeter to read? Use that numerical value as a HI_Limit value. Try setting the analog input value at different levels and see if the output changes in accordance to your input (you can use a 4-20 mA signal generator for that test). You could start by reading this FAQ: How and for which analog measurements can you use the function FC105 "SCALE" to convert the integer values (INT) into real number values? Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 12/22/2011 1:40 AM |
|