8/7/2016 3:36 PM | |
Joined: 9/27/2006 Last visit: 5/11/2024 Posts: 12257 Rating: (2666)
|
Hello Amir; MPI networks allow up to 31 nodes in the single (allowed) segment, max. 50 m. at 187,5 kB. This only takes one connection. Now for the distribution of the 6 available connections shown on page 308 of your manual, you should go to page 309 (see attachment): there are a maximum of 5 OP connections in the CPU 312, and to use them all you need to remove others in the CPU properties (in HWConfig). So you cannot do your project with the CPU you have planned. You could look up the details of available connections in the manual you are looking in, or use the dfollowi ng FAQ that condenses the answers you are looking for (remember these are configurable connections, so you must select them in the CPU properties): What is the maximum number of OPs that a CPU S7-300 can communicate with? https://support.industry.siemens.com/cs/ww/en/view/299124 Hope this helps, Daniel Chartier |
This contribution was helpful to1 thankful Users |
Follow us on