4/3/2024 7:35 AM | |
Joined: 1/25/2024 Last visit: 5/15/2024 Posts: 4 Rating: (0) |
Hello Everyone, TIA portal V18 upd 3, WinCC Adv/Unified PC V18 upd3 The panel I have configured in my project works well when downloaded to an actual device MTP1900, however simulation is not running at all. I get "Download canceled due to a transfer error: 8020AB0019A5FF4". I have checked the forum for similar situation and followed advice from this post but to no avail. I have copied images between folders, as suggested in different threads, updated winCC, repaired the installation and still no success. I attached the list of installed software. |
4/3/2024 9:26 AM | |
Joined: 1/21/2013 Last visit: 5/20/2024 Posts: 2798 Rating: (452)
|
Hi AutEnginerer, If you create a new WinCC Unified device with your installed TIA Portal version, the new device will use device version V18.0.0.3 by default. However, this version requires WinCC Unified PC Runtime V18 - Update 3, which is not installed on your system. You should also check if you are a member of the Windows user groups listed in the manual. Kind regards |
4/3/2024 10:22 AM | |
Joined: 1/25/2024 Last visit: 5/15/2024 Posts: 4 Rating: (0) |
That did the trick, thank you. |