Dear sir, I face one issue from 223-1PL32-0XBO 16 DI /16 DO model I used .I didn't get any voltage from DO side so please help me . (Connection photos I attached please find the attachment) Thanks and regards By Vignesh selvam [snip] ------------------------------------------------------------------------------------------ |
Last edited by: U_6cedb4b9-f995-4c16-88db-c8a6b3ca2d77 at: 04/03/2024 07:11:14Last edited by: Jen_Moderator at: 04/03/2024 12:11:58New subject after splitting Last edited by: Jen_Moderator at: 04/03/2024 12:12:45Contact data removed. |
|
4/3/2024 9:03 PM | |
Joined: 7/7/2010 Last visit: 8/6/2024 Posts: 15059 Rating: (2404)
|
When measuring DC voltage from L on DQ terminals (of all the DI/DQ modules) to M on PLC, do you see ~24VDC? When measuring from M to GND, do you read ~0VDC? When measuring from DQ terminal currently associated with a DigOut that's on (according to the associated green LED) do you see 0V or 24VDC to GND / M (assuming M to GND is 0VDC)? Shine a strong light along side the installed terminals and make sure they are not offset by 1 pin. If a pin is visible on either end, power the system down, remove and correctly reinstall the DQ terminal block(s) as needed so no pin is visible on either end of the terminals (if needed). Post back your results.
|
science guy |
|