5/17/2014 8:42 PM | |
Joined: 11/21/2007 Last visit: 7/25/2025 Posts: 2326 Rating:
|
Hello Stefo You have two options : a) Use a 75mV Shunt in series of 24VDC power circuit. Use a mV to mA Converter transducer ( WIth isolation ) . the mA signal can be connected to a meter / Analog input of a PLC This should be sufficient for upto 1600A Current range I am attaching a drawings extracted from one of the projects where we used Shunt to measure DC current in PLC with good results. b) Hall effect transducers are usually used for higher current> 1000 amps e.g. for Graphite Baking Furnaces, Aluminum / Zinc / CopperElectrolyses etc whe currents can go upto 100kA and beyond. This would of course be a much more expensive that the first option. The Hall effect Transducers usually provide a mA signal proportional to the DC Current which can be connected to a meter / PLC Analog Input Hope this helps Cheers Navnag AttachmentDC_Current_Sensing.pdf (1721 Downloads) |
There is no such thing as the last bug in a program |
|
This contribution was helpful to
2 thankful Users |
5/23/2014 1:46 AM |
|
Posts: 202 Rating:
|
Hi there can you please explain you the shunt that we are connecting to the ammeter has a unit of mV instead of OHM??
|